PublicadoEl 23/11/22 por Comillas
Capítulo de libro

Modeling of steady state fault current contribution of inverter-connected generation in PSS/e

tipo de documento semantico ckh_publication

Ficheros

IIT-21-061A.pdf
Tamaño 452253
Formato Adobe PDF
Fecha de publicación 27/06/2021
Fuente Libro: 14th IEEE PowerTech Conference - PowerTech 2021, Página inicial: 1-6, Página final:
Estado info:eu-repo/semantics/publishedVersion

Resumen

Idioma es-ES
Idioma en-GB
Resumen

This paper presents a method to model steady state fault current contribution of inverter-connected generation such as type 4 wind and PV generators or battery energy storage systems (BESS) in commercially available software packages like PSS/e during three-phase short-circuits. Inverter-connected generation is typically modelled as a negative load or as a generator in these packages. Both representation fail to reflect the current limiting functionality of inverters. The proposed method is based on the Norton equivalent of the generators. The method consists in adding a resonant admittance to cancel out the impact of the equivalent admittance for fault current computation. This way, iterative computations are avoided and no readjustments are needed for different fault locations. The main advantage is that the proposed method is extremely simple to implement. It has been successfully applied to a simple test system, a PV plant, and one of the isolated power systems of the Canary Islands.

Editorial Institute of Electrical and Electronics Engineers Power and Energy Society; Universidad Pontificia C (Madrid, España)
Grupos de investigación y líneas temáticas Instituto de Investigación Tecnológica (IIT)

Palabras clave

Tipo de archivo application/pdf
Idioma en-GB
Tipo de acceso info:eu-repo/semantics/restrictedAccess
Fecha de modificacion 09/09/2022
Fecha de disponibilidad 01/09/2021
fecha de alta 01/09/2021

Categories:

Shared with: